A/D on 16F876
FRANCESC
A/D on 16F876
PostPosted: Mon Jan 26, 2004 6:44 am     Reply with quote
Question
Hi all,
we try to use the PIC 16F876 to read 4 Analog sources connected on ports RA0,RA1,RA2,RA4 (Pins.2,3,4) .Only the four channels read correctly when are connected to Gnd.
Others configurations not represent the correct bit respect the voltage.
If we place that line SETUP_ADC_PORTS(ALL_ANALOG) not have any bit value
Help....How is possible to read correctly the four channels ???
#include <16f873.h>
#device ADC=10
#fuses xt,nowdt,put,nolvp
LONG T,K1,K2,K3,K4;
Main()
SETUP_ADC(ADC_CLOCK_DIV_8);
set_tris_a(0x27);
//SETUP_ADC_PORTS(ALL_ANALOG);
SET_ADC_CHANNEL(0);
T=READ_ADC();
K1=T/64;
SET_ADC_CHANNEL(1);
T=READ_ADC();
K2=T/64;
SET_ADC_CHANNEL(2);
T=READ_ADC();
K3=T/64;
SET_ADC_CHANNEL(4);
T=READ_ADC();
K4=T/64;
Display_bits();
Please Help
KerryW
PostPosted: Mon Jan 26, 2004 8:25 am     Reply with quote
You need a delay between setting the A/D channel and reading the A/D.
SET_ADC_CHANNEL(0);
delay_ms(10); // Delay before reading A/D
T=READ_ADC();
K1=T/64;
itp
PostPosted: Fri Jan 30, 2004 2:30 am     Reply with quote
You have put 10ms delay ??
I have similer problem.
Can anybody help me to setup ADC in my 16F876 uC running at 20Mhz
#include <16F876.h>
#device *=8 ADC=8 /* allow RAM addresses below 255 */
setup_adc_ports(ALL_ANALOG);
setup_adc(ADC_CLOCK_DIV_8);
Is it necessary to put delay?. If so what could be the minimum value.?
Kindly cheak settings given above.
Regards
Itp
PostPosted: Fri Jan 30, 2004 2:59 am     Reply with quote
#include <16F876.h>
Regards
Itp
Read the data sheet...
When working with embedded controllers, you need the data sheet for the chip, as well as the reference documents that go with this (in this case a full example of how to calculate the timings for specific circumstances, is given in the MicroChip 'mid range reference manual').
The time needed, depends on the impedance of the source feeding the pin, and the capacitance of the pin itself (and your tracking in this area), together with the actual accuracy you want to achieve (you can sample 'early', if you are prepared to accept that the last few bits will not be reliable).
If you are feeding the pin from a high impedance source, a very long time may be needed. In part this is why the manufacturers recommend that the maximum source impedance does not exceed 10K.
With this as the maximum input impedance, and assuming that there is fairly negligable external capacitance, a figure of about 20uSec, is the 'required' time.
neil
more to add
PostPosted: Fri Jan 30, 2004 3:28 am     Reply with quote
I will add to Ttelmah's comments....
first, Frances, you have put the ADC setup lines inside your main loop (while(1)). This is not necessary and should be outside the loop, immediately after main(), so it is only executed once. Are there any other setup/config lines missing? What else is your pic doing?
Second. This is a big reason for your ADC not reading correctly. Ttelmah, mentioned this, but I will direct you to Table 11-1 in the datasheet. This shows that the maximum clock frequency for "ADC_DIV_8" can be 5MHz. For anything above this, you will need "ADC_DIV_32". This will cause incomplete reads and has caught me out in the past! Basically, you have to divide the clock frequency further for faster crystal speeds, because of the acquisition time of the ADC due to capacitance.
This should clear things up.
Neil.
itp
PostPosted: Fri Jan 30, 2004 4:31 am     Reply with quote
Hi Ttelmah and neil,
Thank you for your suggestions
Thanks and regards
Itp