I2C communication routines Multi-Master
Mark
PostPosted: Fri Mar 04, 2005 3:51 pm     Reply with quote
Okay, here are the routines. There are 4 files total.
main.c
#case
#include <16F876.h>
#include "SFR16F876.h"
#fuses XT, WDT, NOPROTECT, PUT, BROWNOUT, NOLVP
#define CLOCKFREQUENCY    4000000
#USE DELAY(CLOCK = CLOCKFREQUENCY)
// used for timing stuff - counts up to 0xFF.  Initialized by main()
volatile int8 Milliseconds;
#include "i2c.c"
#include "isr.c"
// Note that yours will be different depending on your hardware
#define  PORT_A_TRIS_MASK        0x0F   /* all inputs except RA4 & RA5      */
#define  PORT_B_TRIS_MASK        0x01   /* all outputs except RB0           */
#define  PORT_C_TRIS_MASK        0xD9   /* all inputs xcept bit 1 (SHIFTREG_CKL)
                                           and bit 2 (SHIFTREG_LOAD)
                                           and bit 5 (Pilot Enable/Reset)   */
  DESCRIPTION:  Handles our milisecond counters
  RETURN: none
  ALGORITHM:  none
  NOTES:  none
void System_Tick(void)
  static int1 LED_State = 0;
  static int16 count=0;
  while (Milliseconds)
    I2C_Timers();
    --Milliseconds;
// This is just a dirty little test to blink an LED on one of my boards
// You wouldn't have anything between these comment lines nor the vars
// declared in the begining
    count++;
    if (count == 1000)
      if (I2C_Tx_Msg.hdr.status == NO_MSG)
        if (LED_State)
          Blink_LED(0x6E,1);
          Blink_LED(0x6E,0);
        LED_State = !LED_State;
      count = 0;
  return;
  DESCRIPTION: This is the "main" function of the input card software.  It
               performs the proper initialization, then starts the main loop
               of the program.
  RETURN:      none
  ALGORITHM:   none
  NOTES:       none
  // Initialize the ports
  set_tris_a(PORT_A_TRIS_MASK);
  set_tris_b(PORT_B_TRIS_MASK);
  set_tris_c(PORT_C_TRIS_MASK);
  // Setup timer2 to int every milisecond.  This is our system tick
  setup_timer_2(T2_DIV_BY_4, 0xFA, 1);
  // Start our time from now
  Milliseconds = 0;
  // Setup the I2C module
  I2C_Initialize();
  I2C_Reset_Hardware();
  // Main loop
  while (TRUE)
    restart_wdt();
    System_Tick();
    // Handle any of our tasks
    I2C_Tasks();
  } // End of forever loop
Mark
PostPosted: Fri Mar 04, 2005 3:52 pm     Reply with quote
i2c.c
/*$F***************************************************************************
* Copyright (C) 2004 Mark Norton and Steve Karg
* Permission is hereby granted, free of charge, to any person obtaining
* a copy of this software and associated documentation files (the
* "Software"), to deal in the Software without restriction, including
* without limitation the rights to use, copy, modify, merge, publish,
* distribute, sublicense, and/or sell copies of the Software, and to
* permit persons to whom the Software is furnished to do so, subject to
* the following conditions:
* The above copyright notice and this permission notice shall be included
* in all copies or substantial portions of the Software.
* THE SOFTWARE IS PROVIDED "AS IS", WITHOUT WARRANTY OF ANY KIND,
* EXPRESS OR IMPLIED, INCLUDING BUT NOT LIMITED TO THE WARRANTIES OF
* MERCHANTABILITY, FITNESS FOR A PARTICULAR PURPOSE AND NONINFRINGEMENT.
* IN NO EVENT SHALL THE AUTHORS OR COPYRIGHT HOLDERS BE LIABLE FOR ANY
* CLAIM, DAMAGES OR OTHER LIABILITY, WHETHER IN AN ACTION OF CONTRACT,
* TORT OR OTHERWISE, ARISING FROM, OUT OF OR IN CONNECTION WITH THE
* SOFTWARE OR THE USE OR OTHER DEALINGS IN THE SOFTWARE.
* Functional
* Description:  Defines the ACCESS.bus implementation for the Microchip
*               microprocessor
* $Log:  $
// Define this to use the hardware MSSP I2C module
//#define USE_HARDWARE
//------------------- Commands Go Here --------------------------------------
#define CMD_BLINK_LED            0x01
//---------------- Define your address here ---------------------------------
#define  MY_I2C_ADDR             0x6E
//------------------- Synchronous Serial Port I2C ---------------------------
#ifdef USE_HARDWARE
  #define  I2C_MASTER_MASK       0x38    // SSPCON.SSPM3-0 = 1000 --
                                         // Master mode, slave idle
#else
  #define  I2C_MASTER_MASK       0x0B    // SSPCON.SSPM3-0 = 1011 --
                                         // firmware master mode, slave idle
#define  I2C_SLAVE_MASK         0x0E    // SSPCON.SSPM3-0 = 1110 --
                                         // slave mode, 7-bit addr, S & P
                                         // interrupts enabled
// This controls the clock speed
#define  I2C_BAUD_100K           100000
#define  I2C_BAUD_400K           400000
#define  I2C_BAUD_VALUE          ((CLOCKFREQUENCY/2)/I2C_BAUD_100K)
#define  I2C_CLK_ENABLE          0x10
#define  I2C_MODE_SETUP          0x20
//---------------------- Message flags ------------------------------------
#define MSGACK                   0xA5
#define MSGNACK                  0xFF
#define MAX_TRIES                10     // max number to attempt tx message
//--------------------- Message Status --------------------------------------
enum MSG_STATUS
  NO_MSG,
  MSG_READY,
  MSG_ERROR,
  CHECKSUM_OK
// For the PIC18's we will use the LAT registers
#if defined(__PCH__)
  #define I2C_CLK_LATCH         LATCbits.LATC3
  #define I2C_DATA_LATCH        LATCbits.LATC4
#else
  #define I2C_CLK_LATCH         PORTCbits.RC3
  #define I2C_DATA_LATCH        PORTCbits.RC4
#define I2C_CLK                 PORTCbits.RC3
#define I2C_DATA                PORTCbits.RC4
#define I2C_CLK_HI_Z            TRISCbits.TRISC3
#define I2C_SDA_HI_Z            TRISCbits.TRISC4
// Used to define the amount of data for largest command
#define MAX_MSG_LEN             10
union I2C_MSG
  struct
    enum MSG_STATUS status;   // Status
    int8 dest;                // Message destination
    int8 src;                 // Message source
    int8 len;                 // Message length
    int8 opcode;              // Message command
    int8 data[MAX_MSG_LEN];   // Message data
  } hdr;
  int8 buf[MAX_MSG_LEN + 5];
//--------------------- I2C recieve states -----------------------------------
enum I2C_RX_STATES
  I2C_IDLE,
  I2C_RxING,
  I2C_SLAVE_TxING,
  I2C_TxING,
  I2C_WAITING
enum I2CRESULTS
  BYTE_NACKED,
  BYTE_ACKED,
  LOST_ARBITRATION,
  NO_RESPONSE,
  MSG_TRANSMITTED
typedef enum I2CRESULTS I2C_RESULTS;
//----------------------------- globals -------------------------------------
// I2C recieved buffer
union I2C_MSG I2C_Rx_Msg;
// I2C transmit buffer
union I2C_MSG I2C_Tx_Msg;
// Status of I2C bus
enum I2C_RX_STATES I2C_State = I2C_IDLE;
// wait time before sending a message
int8 I2C_Wait_To_Send;
//----------------------------- locals -------------------------------------
// this is our current i2c address
static int8 I2C_Address = MY_I2C_ADDR;
// used to timeout receiving a message
static int8 I2C_Bus_Timeout;
* DESCRIPTION: Send a byte across the i2c bus.
* RETURN:      Three possible states (ACKed, NAKed, Lost Arbitratiom)
* ALGORITHM:   none
* NOTES:       none
static I2C_RESULTS I2C_Write(
  int8 data) // byte sent over the I2C
#ifdef USE_HARDWARE
  SSPBUF = (data);
  while (SSPSTATbits.BF)
    #asm
    nop
    #endasm
  // Wait until the bus is idle
  while ((SSPCON2 & 0x1F) || (SSPSTATbits.R_W));
  if (PIR2bits.BCLIF)           // test for bus collision
    return (LOST_ARBITRATION);          // return with Bus Collision error
  if ( !SSPCON2bits.ACKSTAT )   // test for ACK condition received
    return(BYTE_ACKED);
    return(BYTE_NACKED);
#else
  I2C_RESULTS value;       // Value to be returned
  int8 i;                  // Index to counter
  int8 loop_count;         // Clock stretch loop counter
  I2C_CLK_LATCH=0;
  I2C_DATA_LATCH=0;
  for (i=0; i<8; i++)
    delay_us(5);
    I2C_CLK_HI_Z=0;
    if (data & 0x80)
      I2C_SDA_HI_Z=1;
      delay_us(3);
      if (!I2C_DATA)
        I2C_CLK_HI_Z=1;
      I2C_SDA_HI_Z=0;
      delay_us(3);
    delay_us(5);
    I2C_CLK_HI_Z=1;
    //  Allow the clock to be stretched
    loop_count = 255;
    while (loop_count > 0)
      if (I2C_CLK)
      --loop_count;
      delay_us(1);
    data <<= 1;
  delay_us(6);
  I2C_CLK_HI_Z=0;
  delay_us(1);
  I2C_SDA_HI_Z=0;
  delay_us(1);
  I2C_SDA_HI_Z=1;
  delay_us(4);
  I2C_CLK_HI_Z=1;
  loop_count = 255;
    if (I2C_CLK)
    --loop_count;
    delay_us(1);
  if (I2C_DATA)
    value = BYTE_NACKED;
    value = BYTE_ACKED;
  delay_us(5);
  I2C_CLK_HI_Z=0;
  delay_us(1);
  I2C_SDA_HI_Z=0;
  return (value);
* DESCRIPTION: Sends a START condition over the i2c bus
* ALGORITHM:   none
* NOTES:       none
static I2C_RESULTS I2C_Start(void)
#ifdef USE_HARDWARE
  SSPCON2bits.SEN = 1;
  while (SSPCON2bits.SEN)
    #asm
    nop
    #endasm
  return (BYTE_ACKED);
#else
  // Set both lines to inputs
  I2C_SDA_HI_Z=1;
  delay_us(1);
  I2C_CLK_HI_Z=1;
  // Check for a low condition on the data line.  If it is low then someone
  // else is already communicating so exit
  if (!I2C_DATA)
  loop_count = 255;
    if (I2C_CLK)
    --loop_count;
    delay_us(1);
  // If loop count is 0 then the clock was held low for more than 255us
  // so exit with an arbitration error
  if (loop_count == 0)
  I2C_SDA_HI_Z=0;
  I2C_DATA_LATCH=0;
  delay_us(2);
  I2C_CLK_HI_Z=0;
  I2C_CLK_LATCH=0;
* DESCRIPTION: Sends a START condition over the I2C
* ALGORITHM:   none
* NOTES:       none
static I2C_RESULTS I2C_Restart(void)
#ifdef USE_HARDWARE
  SSPCON2bits.RSEN = 1;
  while (SSPCON2bits.RSEN)
    #asm nop #endasm
#else
  return(I2C_Start());
* DESCRIPTION: Sends a STOP condition over the I2C
* RETURN:      none
* ALGORITHM:   none
* NOTES:       none
static void I2C_Stop(void)
#ifdef USE_HARDWARE
  SSPCON2bits.PEN = 1;
  while (SSPCON2bits.PEN)
    #asm nop #endasm
#else
  I2C_CLK_HI_Z=0;
  I2C_CLK_LATCH=0;
  delay_us(1);
  I2C_SDA_HI_Z=0;
  I2C_DATA_LATCH=0;
  delay_us(4);
  I2C_CLK_HI_Z=1;
  loop_count = 255;
    delay_us(1);
    if (I2C_CLK)
    --loop_count;
  I2C_SDA_HI_Z=1;
* DESCRIPTION: Reads a byte from the ACCESS.bus i2c.
* RETURN:      byte of data from the ACCESS.bus
* ALGORITHM:   none
* NOTES:       bit bang the i2c
static int8 I2C_Read(
  int8 read_ack) // TRUE if we should ACK the byte
#ifdef USE_HARDWARE
  SSPCON2bits.RCEN = 1;
  while (SSPCON2bits.RCEN)
    #asm nop #endasm
  SSPCON2bits.ACKDT = read_ack;
  SSPCON2bits.ACKEN = 1;
  while (SSPCON2bits.ACKEN)
    #asm nop #endasm
  return(SSPBUF);
#else
  int8 value=0;       // Value to be returned
  I2C_SDA_HI_Z=1;
  delay_us(1);
  I2C_SDA_HI_Z=1;
  I2C_DATA_LATCH=0;
  I2C_CLK_LATCH=0;
  for (i=0; i<8; i++)
    delay_us(10);
    I2C_CLK_HI_Z=1;
    value <<= 1;
    loop_count = 255;
      if (I2C_CLK)
      --loop_count;
      delay_us(1);
    delay_us(5);
    if (I2C_DATA)
      value |= 0x01;
      value &= ~0x01;
    delay_us(8);
    I2C_CLK_HI_Z=0;
  delay_us(4);
  if (read_ack > 0)
    I2C_SDA_HI_Z=0;
  delay_us(5);
  I2C_CLK_HI_Z=1;
  delay_us(10);
  I2C_CLK_HI_Z=0;
  delay_us(1);
  I2C_SDA_HI_Z=0;
  return (value);
* DESCRIPTION: Clears the SSPBUF register
* RETURN:      none
* ALGORITHM:   none
* NOTES:       none
#inline
void I2C_Clear_SSPBUF(void)
  int8 dummy;
  dummy = SSPBUF;
  (void)dummy;
  return;
* DESCRIPTION: Resets the ACCESS.bus hardware to a known state
* RETURN:      none
* ALGORITHM:   none
* NOTES:       none
void I2C_Reset_Hardware(void)
  // Reset the I2C if we timeout, this should prevent us from ever
  // locking up the I2C
  I2C_CLK_HI_Z=1;
  I2C_SDA_HI_Z=1;
  SSPADD = I2C_Address;
  SSPCON = (I2C_SLAVE_MASK);
  SSPCON = (I2C_SLAVE_MASK | I2C_CLK_ENABLE | I2C_MODE_SETUP);
  // Clear the buffer
  I2C_Clear_SSPBUF();
  SSPCONbits.SSPOV = 0;
  clear_interrupt(INT_SSP);
  enable_interrupts(INT_SSP);
  return;
* DESCRIPTION: Sets our ACESS.bus address
* RETURN:      none
* ALGORITHM:   none
* NOTES:       none
void I2C_Set_Address(
  int8 address) // our new address
  SSPADD = I2C_Address = address;
* DESCRIPTION: Initialize our module level variables
* RETURN:      none
* ALGORITHM:   none
* NOTES:       none
void I2C_Initialize(void)
  int8 temp_intcon;
  // Save the current interrupt state
  temp_intcon = INTCON;
  // Make sure that the interrupts are disabled
  disable_interrupts(GLOBAL);
  I2C_Set_Address(MY_I2C_ADDR);
  I2C_Rx_Msg.hdr.status = NO_MSG;
  I2C_Tx_Msg.hdr.status = NO_MSG;
  I2C_Wait_To_Send = 0;
  // Restore the previous interrupt state
  INTCON = temp_intcon;
* DESCRIPTION: Allows our I2C timers to increment/decrement
* RETURN:      none
* ALGORITHM:   none
* NOTES:       called every mS
void I2C_Timers(void)
  if (I2C_Bus_Timeout)
    --I2C_Bus_Timeout;
  // haven't received a byte in a long time
  else if (I2C_State > I2C_RxING)
    // reset the bus if the buffer is full
    if (SSPSTATbits.BF)
* DESCRIPTION: Processes the messages received on the I2C
* RETURN:      none
* ALGORITHM:   none
* NOTES:       none
void I2C_Process_Message(
  union I2C_MSG* buf,
  int8 len)
  // not ready to process yet
  if (buf->hdr.status != MSG_READY)
    return;
  // Disable access bus interrupt since we are processing a message
  disable_interrupts(INT_SSP);
  // Go ahead and release the buffer.  We won't receive anything yet
  // since we disabled the interrupt above
  buf->hdr.status = NO_MSG;
  // ------------------------- Add your commands here -----------------------
  switch (buf->hdr.opcode)
    // Test command for blinking an LED
    case CMD_BLINK_LED:
        if (buf->buf[5] == 0)
          PORTAbits.RA4 = 0;
          PORTAbits.RA4 = 1;
    default:
  // Turn back on the access bus interrupt
  return;
* DESCRIPTION: Handles the bus reception.
* RETURN:      none
* ALGORITHM:   none
* NOTES:       none
#inline
void I2C_Rx_Byte(void)
  static int8 rx_count = 0;             // num of bytes received
  static signed int8 rx_msg_len = 0;    // msg length
  static int8 checksum = 0;             // message checksum (XOR)
  static int8 data = 0;                 // data read from SSPBUF
  // Check for a stop bit
  if (SSPSTATbits.P)
    // inter-message wait time in ms
    I2C_Wait_To_Send = 5;
    I2C_Bus_Timeout = 0;
    // were we addressed in read mode
    if (SSPSTATbits.R_W)
      if (I2C_Rx_Msg.hdr.status == CHECKSUM_OK)
        I2C_Rx_Msg.hdr.status = MSG_READY;
        // Load acknowledgement value
        SSPBUF = MSGACK;
        SSPBUF = MSGNACK;
      // Setup to allow data to be read from us
      SSPCONbits.CKP=1;
      I2C_State = I2C_SLAVE_TxING;
      I2C_Bus_Timeout = 25;
    // See if we were addressed
    // The following line was modified because of errata with
    // the PIC18CXX2 clearing the BF bit when the BSR is pointed to 0x0F
    // and an instruction contains 0xC9 in its 8 least significant bits
//    else if (SSPSTATbits.BF)
    else if ((SSPSTATbits.BF) || (I2C_State == I2C_RxING))
      // continue recieving bytes
      // process the first byte
      if (!SSPSTATbits.D_A)
        // Read the data
        data = SSPBUF;
        I2C_State = I2C_RxING;
        I2C_Rx_Msg.hdr.dest = data;
        rx_msg_len = 2;
        rx_count = 1;
        checksum = data;
        // Read the data
        data = SSPBUF;
        ++rx_count;                             // keep track of how many bytes
        if (rx_count == 3)                      // test for length of msg byte
          rx_msg_len = data;                    // set length counter
          --rx_msg_len;
        if (rx_msg_len == -1)                   // check for end of msg
          I2C_State = I2C_WAITING;
          if ((checksum ^ data) == 0)
            I2C_Rx_Msg.hdr.status = CHECKSUM_OK;
        checksum ^= data;
        if (rx_count < sizeof(I2C_Rx_Msg.buf))
          I2C_Rx_Msg.buf[rx_count] = data;
* DESCRIPTION: Transmits messages out the I2C port
* RETURN:      FALSE on failure    TRUE on success
* ALGORITHM:   none
* NOTES:       none
int8 I2C_Send_Msg(
  int8* buf,       // buffer containing the msg to send
  int8 len)        // length of the buffer
  int8 msg_count       = 0;           // number of times tx attempted
  int8 checksum        = 0;           // XOR of each byte in the msg
  int8 length          = 0;           // length of msg being sent
  int8 i               = 0;           // index to counter
  int8 readdata        = 0;           // data read from destination
  int8 device_present  = FALSE;       // determines if the rxing device is there
  I2C_RESULTS result   = BYTE_ACKED;  // return result from our I2C functions
  // The length of the message is the 4th byte
  length = buf[3];
  // Make sure the buffer is big enough.  The true length is 4 more bytes
  // than the msg length
  if (len < (length + 4))
    buf[0] = NO_MSG;
    return(FALSE);
  // Wait until this timer expires, this could be due to receiving bytes
  // or a delay between messages
  while (TRUE)
    restart_wdt();
    // Check to see if we are receiving a message.  If so, then exit
    if (I2C_State != I2C_IDLE)
      return(FALSE);
    // See if we are still waiting
    if (!I2C_Wait_To_Send)
  // limit the number of times to try and send the message
  for (msg_count = 0; msg_count < MAX_TRIES; msg_count++)
    if (result == LOST_ARBITRATION)
      return(FALSE);
    // The last action was not a stop condition so either the hardware
    // was reset or there was some sort of error.  We will check to see
    // if the bus is free.
    if (!SSPSTATbits.P)
      restart_wdt();
        return(FALSE);
      // We will monitor the SCL line for 2 ms to see if it goes low.
      // if it does, then someone is talking so exit.
      I2C_Wait_To_Send = 2;
      while (I2C_Wait_To_Send)
        if (!I2C_CLK)
          return(FALSE);
    I2C_State = I2C_TxING;
    SSPCON = (I2C_MASTER_MASK | I2C_CLK_ENABLE);
    SSPADD = I2C_BAUD_VALUE;
    // Lets make sure the Interrupt flag for Bus collision is clear
    clear_interrupt(INT_BUSCOL);
    buf[0] = NO_MSG;
    checksum = 0;
    // The true message length is 4 bytes longer
    for (i = 1; i < (length + 4); i++)
      if (i==1)
        result = I2C_Start();
        if (result != BYTE_ACKED)
      checksum ^= buf[i];
      // If the receiving device fails to acknowledge a byte then clear
      // the var i to signal that there was a problem
      result = I2C_Write(buf[i]);
      delay_us(50);
      device_present = TRUE;
      if (i==(length + 3))
        result = I2C_Write(checksum);
        // Start of the message received acknowledgement
        result = I2C_Restart();
        result = I2C_Write(buf[1] | 0x01);
        readdata = I2C_Read(0);
    if (result != LOST_ARBITRATION)
      I2C_Stop();
    if ((result == BYTE_ACKED) && (readdata == MSGACK))
      buf[0] = NO_MSG;
      return(TRUE);
  // if the other device never ACKed the message, then its probably not there so
  // lets consider the message sent.
  if (!device_present)
    buf[0] = NO_MSG;
    return(TRUE);
  return(FALSE);
* DESCRIPTION: Allows our I2C tasks to run
* RETURN:      none
* ALGORITHM:   none
* NOTES:       none
void I2C_Tasks(void)
  // See if we have received any messages
  I2C_Process_Message(&I2C_Rx_Msg, sizeof(I2C_Rx_Msg.buf));
  // Check for an overflow condition
  if (SSPCONbits.SSPOV)
    // Overflow occured so reset the I2C
  // Transmit any messages
  if (I2C_Tx_Msg.hdr.status != NO_MSG)
    (void)I2C_Send_Msg(I2C_Tx_Msg.buf, sizeof(I2C_Tx_Msg.buf));
* DESCRIPTION: Sends the output level to address dest.
* RETURN:      none
* ALGORITHM:   none
* NOTES:       none
void Blink_LED(
  int8 dest, // destination address for message
  int8 level) // level that is being sent
  I2C_Tx_Msg.hdr.status = MSG_READY;
  I2C_Tx_Msg.hdr.dest = dest;
  I2C_Tx_Msg.hdr.src = I2C_Address;
  I2C_Tx_Msg.hdr.len = 2;
  I2C_Tx_Msg.hdr.opcode = CMD_BLINK_LED;
  I2C_Tx_Msg.hdr.data[0] = level;             /* Level to set the output */
  return;
Mark
isr.c
* NAME:        Interrupt_SSP
* DESCRIPTION: Invoked whenever the dest address in an ABus
*              AB message if one has occurred.
* PARAMETERS:  none
* RETURN:      none
* ALGORITHM:   none
* NOTES:       none
#int_ssp
static void Interrupt_SSP(void)
  /* Make sure the buffer has not overflowed */
    // don't recieve a byte if we are already processing a msg
    if (I2C_Rx_Msg.hdr.status != MSG_READY)
      I2C_Rx_Byte();
  return;
* NAME:        Interrupt_Timer2
* DESCRIPTION: Timer2 is set to go off every 1ms.
* PARAMETERS:  none
* RETURN:      none
* ALGORITHM:   none
* NOTES:       none
#int_timer2
static void Interrupt_Timer2(void)
  // Global Milisecond timer
  if (Milliseconds < 0xFF)
    ++Milliseconds;
  //------- These are waitable timers so they must be done in the ISR ----------/
  // Decrement timers
  if (I2C_Wait_To_Send)
    --I2C_Wait_To_Send;
Mark
PostPosted: Fri Mar 04, 2005 3:53 pm     Reply with quote
sfr16f876.h
#ifndef SFR16F876_H
#define SFR16F876_H
#nolist
unsigned char ADCON0;
#locate ADCON0=0x1F
struct {
    unsigned char ADON:1;
    unsigned char UNUSED0:1;
    unsigned char GO_DONE:1;
    unsigned char CHS0:1;
    unsigned char CHS1:1;
    unsigned char CHS2:1;
    unsigned char ADCS0:1;
    unsigned char ADCS1:1;
} ADCON0bits;
#locate ADCON0bits=0x1F
unsigned char ADCON1;
#locate ADCON1=0x9F
struct {
    unsigned char PCFG0:1;
    unsigned char PCFG1:1;
    unsigned char PCFG2:1;
    unsigned char PCFG3:1;
    unsigned char UNUSED:3;
    unsigned char ADFM:1;
} ADCON1bits ;
#locate ADCON1bits=0x9F
unsigned char ADRESH;
#locate ADRESH=0x1E
unsigned char ADRESL;
#locate ADRESL=0x9E
unsigned char CCP1CON;
#locate CCP1CON=0x17
struct {
    unsigned char CCP1M0:1;
    unsigned char CCP1M1:1;
    unsigned char CCP1M2:1;
    unsigned char CCP1M3:1;
    unsigned char CCP1Y:1;
    unsigned char CCP1X:1;
} CCP1CONbits ;
#locate CCP1CONbits=0x17
unsigned char CCP2CON;
#locate CCP2CON=0x1D
struct {
    unsigned char CCP2M0:1;
    unsigned char CCP2M1:1;
    unsigned char CCP2M2:1;
    unsigned char CCP2M3:1;
    unsigned char CCP2Y:1;
    unsigned char CCP2X:1;
} CCP2CONbits ;
#locate CCP2CONbits=0x1D
unsigned int16 CCPR1;
#locate CCPR1=0x15
unsigned char CCPR1H;
#locate CCPR1H=0x16
unsigned char CCPR1L;
#locate CCPR1L=0x15
unsigned int16 CCPR2;
#locate CCPR2=0x1B
unsigned char CCPR2H;
#locate CCPR2H=0x1C
unsigned char CCPR2L;
#locate CCPR2L=0x1B
unsigned char EEADR;
#locate EEADR=0x10D
unsigned char EECON1;
#locate EECON1=0x18C
struct {
    unsigned char RD:1;
    unsigned char WR:1;
    unsigned char WREN:1;
    unsigned char WRERR:1;
    unsigned char EEPGD:1;
} EECON1bits ;
#locate EECON1bits=0x18C
unsigned char EECON2;
#locate EECON2=0x18D
unsigned char EEDATA;
#locate EEDATA=0x10C
unsigned char EEDATH;
#locate EEDATA=0x10E
unsigned char EEADRH;
#locate EEDATA=0x10F
unsigned char FSR;
#locate FSR=0x04
unsigned char INDF;
#locate INDF=0x00
unsigned char INTCON;
#locate INTCON=0x0B
struct
  unsigned char RBIF:1;
  unsigned char INTF:1;
  unsigned char T0IF:1;
  unsigned char RBIE:1;
  unsigned char INTE:1;
  unsigned char T0IE:1;
  unsigned char PEIE:1;
  unsigned char GIE:1;
} INTCONbits;
#locate INTCONbits=0x0B
unsigned char OPTION;
#locate OPTION=0x81
struct
  unsigned char PS0:1;
  unsigned char PS1:1;
  unsigned char PS2:1;
  unsigned char PSA:1;
  unsigned char T0SE:1;
  unsigned char T0CS:1;
  unsigned char INTEDG:1;
  unsigned char NOT_RBPU:1;
} OPTIONbits;
#locate OPTIONbits=0x81
unsigned char PCL;
#locate RCON=0x02
unsigned char PCLATH;
#locate RCON=0x0A
unsigned char PCON;
#locate RCON=0x8E
struct
  unsigned char NOT_BOR:1;
  unsigned char NOT_POR:1;
} PCONbits ;
#locate PCONbits=0x8E
unsigned char PIE1;
#locate PIE1=0x8C
struct {
    unsigned char TMR1IE:1;
    unsigned char TMR2IE:1;
    unsigned char CCP1IE:1;
    unsigned char SSPIE:1;
    unsigned char TXIE:1;
    unsigned char RCIE:1;
    unsigned char ADIE:1;
    unsigned char PSPIE:1;
} PIE1bits ;
#locate PIE1bits=0x8C
unsigned char PIE2;
#locate PIE2=0x8D
struct {
    unsigned char CCP2IE:1;
    unsigned char UNUSED0:2;
    unsigned char BCLIE:1;
    unsigned char EEIE:1;
} PIE2bits ;
#locate PIE2bits=0x8D
unsigned char PIR1;
#locate PIR1=0x0C
struct {
    unsigned char TMR1IF:1;
    unsigned char TMR2IF:1;
    unsigned char CCP1IF:1;
    unsigned char SSPIF:1;
    unsigned char TXIF:1;
    unsigned char RCIF:1;
    unsigned char ADIF:1;
    unsigned char PSPIF:1;
} PIR1bits ;
#locate PIR1bits=0x0C
unsigned char PIR2;
#locate PIR2=0x0D
struct {
    unsigned char CCP2IF:1;
    unsigned char BCLIF:1;
    unsigned char EEIF:1;
} PIR2bits ;
#locate PIR2bits=0x0D
unsigned char PORTA;
#locate PORTA=0x05
struct
  unsigned char RA0:1;
  unsigned char RA1:1;
  unsigned char RA2:1;
  unsigned char RA3:1;
  unsigned char RA4:1;
  unsigned char RA5:1;
  unsigned char RA6:1;
} PORTAbits ;
#locate PORTAbits=0x05
unsigned char PORTB;
#locate PORTB=0x06
struct
  unsigned char RB0:1;
  unsigned char RB1:1;
  unsigned char RB2:1;
  unsigned char RB3:1;
  unsigned char RB4:1;
  unsigned char RB5:1;
  unsigned char RB6:1;
  unsigned char RB7:1;
} PORTBbits ;
#locate PORTBbits=0x06
unsigned char PORTC;
#locate PORTC=0x07
struct
  unsigned char RC0:1;
  unsigned char RC1:1;
  unsigned char RC2:1;
  unsigned char RC3:1;
  unsigned char RC4:1;
  unsigned char RC5:1;
  unsigned char RC6:1;
  unsigned char RC7:1;
} PORTCbits ;
#locate PORTCbits=0x07
unsigned char PORTD;
#locate PORTD=0x08
struct
  unsigned char RD0:1;
  unsigned char RD1:1;
  unsigned char RD2:1;
  unsigned char RD3:1;
  unsigned char RD4:1;
  unsigned char RD5:1;
  unsigned char RD6:1;
  unsigned char RD7:1;
} PORTDbits ;
#locate PORTDbits=0x08
unsigned char PORTE;
#locate PORTE=0x09
struct
  unsigned char RE0:1;
  unsigned char RE1:1;
  unsigned char RE2:1;
} PORTEbits ;
#locate PORTEbits=0x09
unsigned char PR2;
#locate PR2=0x92
unsigned char RCREG;
#locate RCREG=0x1A
unsigned char RCSTA;
#locate RCSTA=0x18
struct {
    unsigned char RX9D:1;
    unsigned char OERR:1;
    unsigned char FERR:1;
    unsigned char ADDEN:1;
    unsigned char CREN:1;
    unsigned char SREN:1;
    unsigned char RX9:1;
    unsigned char SPEN:1;
} RCSTAbits ;
#locate RCSTAbits=0x18
unsigned char SPBRG;
#locate SPBRG=0x99
unsigned char SSPADD;
#locate SSPADD=0x93
unsigned char SSPBUF;
#locate SSPBUF=0x13
unsigned char SSPCON;
#locate SSPCON=0x14
struct {
    unsigned char SSPM0:1;
    unsigned char SSPM1:1;
    unsigned char SSPM2:1;
    unsigned char SSPM3:1;
    unsigned char CKP:1;
    unsigned char SSPEN:1;
    unsigned char SSPOV:1;
    unsigned char WCOL:1;
} SSPCONbits ;
#locate SSPCONbits=0x14
unsigned char SSPCON2;
#locate SSPCON2=0x91
struct {
    unsigned char SEN:1;
    unsigned char RSEN:1;
    unsigned char PEN:1;
    unsigned char RCEN:1;
    unsigned char ACKEN:1;
    unsigned char ACKDT:1;
    unsigned char ACKSTAT:1;
    unsigned char GCEN:1;
} SSPCON2bits ;
#locate SSPCON2bits=0x91
unsigned char SSPSTAT;
#locate SSPSTAT=0x94
struct {
    unsigned char BF:1;
    unsigned char UA:1;
    unsigned char R_W:1;
    unsigned char S:1;
    unsigned char P:1;
    unsigned char D_A:1;
    unsigned char CKE:1;
    unsigned char SMP:1;
} SSPSTATbits ;
#locate SSPSTATbits=0x94
unsigned char STATUS;
#locate STATUS=0x03
struct {
    unsigned char C:1;
    unsigned char DC:1;
    unsigned char Z:1;
    unsigned char NOT_PD:1;
    unsigned char NOT_TO:1;
    unsigned char RP0:1;
    unsigned char RP1:1;
    unsigned char IRP:1;
} STATUSbits ;
#locate STATUSbits=0x03
unsigned char T1CON;
#locate T1CON=0x10
struct
  unsigned char TMR1ON:1;
  unsigned char TMR1CS:1;
  unsigned char NOT_T1SYNC:1;
  unsigned char T1OSCEN:1;
  unsigned char T1CKPS0:1;
  unsigned char T1CKPS1:1;
} T1CONbits ;
#locate T1CONbits=0x10
unsigned char T2CON;
#locate T2CON=0x12
struct {
    unsigned char T2CKPS0:1;
    unsigned char T2CKPS1:1;
    unsigned char TMR2ON:1;
    unsigned char TOUTPS0:1;
    unsigned char TOUTPS1:1;
    unsigned char TOUTPS2:1;
    unsigned char TOUTPS3:1;
} T2CONbits ;
#locate T2CONbits=0x12
unsigned char TMR0;
#locate TMR0=0x01
unsigned int16 TMR1;
#locate TMR1=0x0E
unsigned char TMR1H;
#locate TMR1H=0x0F
unsigned char TMR1L;
#locate TMR1L=0x0E
unsigned char TMR2;
#locate TMR2=0x11
unsigned char TRISA;
#locate TRISA=0x85
struct {
    unsigned char TRISA0:1;
    unsigned char TRISA1:1;
    unsigned char TRISA2:1;
    unsigned char TRISA3:1;
    unsigned char TRISA4:1;
    unsigned char TRISA5:1;
} TRISAbits ;
#locate TRISAbits=0x85
unsigned char TRISB;
#locate TRISB=0x86
struct {
    unsigned char TRISB0:1;
    unsigned char TRISB1:1;
    unsigned char TRISB2:1;
    unsigned char TRISB3:1;
    unsigned char TRISB4:1;
    unsigned char TRISB5:1;
    unsigned char TRISB6:1;
    unsigned char TRISB7:1;
} TRISBbits ;
#locate TRISBbits=0x86
unsigned char TRISC;
#locate TRISC=0x87
struct {
    unsigned char TRISC0:1;
    unsigned char TRISC1:1;
    unsigned char TRISC2:1;
    unsigned char TRISC3:1;
    unsigned char TRISC4:1;
    unsigned char TRISC5:1;
    unsigned char TRISC6:1;
    unsigned char TRISC7:1;
} TRISCbits ;
#locate TRISCbits=0x87
unsigned char TRISD;
#locate TRISD=0x88
struct {
    unsigned char TRISD0:1;
    unsigned char TRISD1:1;
    unsigned char TRISD2:1;
    unsigned char TRISD3:1;
    unsigned char TRISD4:1;
    unsigned char TRISD5:1;
    unsigned char TRISD6:1;
    unsigned char TRISD7:1;
} TRISDbits ;
#locate TRISDbits=0x88
unsigned char TRISE;
#locate TRISE=0x89
struct {
    unsigned char TRISE0:1;
    unsigned char TRISE1:1;
    unsigned char TRISE2:1;
    unsigned char PSPMODE:1;
    unsigned char IBOV:1;
    unsigned char OBF:1;
    unsigned char IBF:1;
} TRISEbits ;
#locate TRISEbits=0x89
unsigned char TXREG;
#locate TXREG=0x19
unsigned char TXSTA;
#locate TXSTA=0x98
struct {
    unsigned char TX9D:1;
    unsigned char TRMT:1;
    unsigned char BRGH:1;
    unsigned char UNUSED:1;
    unsigned char SYNC:1;
    unsigned char TXEN:1;
    unsigned char TX9:1;
    unsigned char CSRC:1;
} TXSTAbits ;
#locate TXSTAbits=0x98
#list
#endif  /* SFR16F876_H */