PID question. Sampling frequency?
valemike
PostPosted: Tue Sep 14, 2004 9:18 am     Reply with quote
I'm using pin RB0 as a zero cross detector from the AC line.
My period for the heater is 8 cycles (thus 8 x 16.6ms = 133ms).
The duty cycle is 0 thru 8, giving me a fraction of n/8.
If doing PID regulation, how often do I have to sample the temperature? Everytime the 8 cycles has elapsed? Or more often, less often?
Re: PID question. Sampling frequency?
PostPosted: Tue Sep 14, 2004 9:45 am     Reply with quote
It depends on other things. How quickly the sensor responds to changes in the temperature, how fast the heater responds etc.. If the system has a 'slow' response time, you can sample at a much lower frequency. If however the response if fast, then the 'control loop' also needs to be fast.
The loop time, needs to be significantly faster than the system response time, or oscillation is likely.
SherpaDoug
PostPosted: Tue Sep 14, 2004 9:55 am     Reply with quote
In your case once per eight cycles would be ideal, preferably near the end of cycle eight when the heater is almost allways off. For a heater it doesn't matter much but if it was an electrically noisy load like a motor it is especially good to sample when the load is off.
If you were to sample every 7 or 9 cycles you could get a "beat note" between the PWM cycles and the sampling cycles that can cause problems. Keep the sampling a constant multiple (or sub-multiple) of the PWM cycle.