Zezem
CCS compiler overwriting SFRs |
Posted: Mon Jun 25, 2018 4:39 pm |
I'm pretty sure I saw something related to this on this forum and was just wondering if someone had an solution.
Right now I have a program that keeps assigning float variables to weird memory addresses. They are trying to store them in SFR locations 0xF81-0xF83.
Because of this the float values aren't being written to and always outputting 0.0000.
If I make a duplicate of the floating points giving me my problem, and just leave the original variables untouched. The duplicate floating points will get assigned a proper register value and everything will work fine.
I read somewhere on here that it might be my compiler version but I was seeing if there was another way to fix this problem.
compiler version 5.046
F81-F84 pump_voltage
F81 PORTB
F81.1 WRITE
F82-F85 _24VDC
F82.0 READ
F82 PORTC
F82.7 Test_Pin
F83 PORTD
F84 PORTE
F85-F88 pump_current
F89 LATA
F8A LATB
F8B LATC
F8C LATD
// Filename: MAIN.C
// Function Name: main()
// Author: PGS
// Description: Main loop of Flow Cell Control uP PIC18F26K22
#include "18F26k22.h"
#device ICD=TRUE
#fuses HSM, WDT, PUT, NOPLLEN, BROWNOUT, CCP2C1, PROTECT
//#include "Flow_Params.h"
//#include "f_proto.h"
#include "globals.h"
#include "defines.h"
#include "f26k22_regs.h"
#include "math.h"
#include "stdlib.h"
#id CHECKSUM
#use delay(clock=4000000, RESTART_WDT)
#use standard_io(B)
#use standard_io(C)
#use rs232(baud=1000,FLOAT_HIGH,xmit=PIN_B1,rcv=PIN_C0)
#include "init.c"
#include "isr_t1.c"
//#include "i2c.c"
//#include "wr_1803.c" //Write/Read to DS1803 Digital Pot
//#include "medley.c" //Misc utilities, mostly pot adjustments for temp/pressure
//compensation
//#include "RS232_RXTX.c" //"White Wire Interface" functions and commands
#include "ad_read.c" //A->D read utility, called by "rd_sig.c"
#include "rd_sig.c" //Reads one of 10 analog channels "read_a_signal(CH)"
//Also adjusts Pot settings "set_a_signal(CH)"
//#include "cal_sw.c"
//#include "wr_unit_param.c"
//#include "rd_unit_param.c"
#include "Err_Chk.c"
//#include "Param_Default_Flow.h"
// static byte stored_error_code;
// static byte stored_unit_status;
// static short main_fault_sw_status;
// int8 degrees_modulator=0, offset;
int16 degrees_raw, prev_degrees_raw=0;
int16 pump_voltage_raw;
int16 _24VDC_raw;
int16 pump_current_raw;
int16 temp16;
// MAIN()
// int8 temp8;
int8 bytes_recvd;
initialize();
// read_eeprom_data(); // get stored calibration values
restart_wdt();
//temp8 = compute_checksum();
//delay_us(1);
/* // check after 1st eeprom read
if(header_byte != HEADER_BYTE_VALUE)
error_code1= ERR_EEPROM_HEADER_BYTE;
else if(eeprom_checksum != compute_checksum())
error_code1= ERR_EEPROM_CHKSUM;
if(error_code1) // power-up fault on 1st read?
error_code1= CLEAR; // clear error code from 1st read
read_eeprom_data(); // read eeprom 2nd time FIX
restart_wdt();
// check after 2nd eeprom read
if(error_code1) // power up fault on 2nd read?
Restore_Factory_Param();
err_check();
GIE = OFF;
//unit_status = 0;
//=====================================MAIN LOOP==================================
for(;;) //MAIN LOOP
restart_wdt();
Test_Pin = ~Test_Pin;
//===================== Read Temperature ===================================
//current degrees is 10 bit number, LM50=10mv/degree C on a 0.5V bias
degrees_raw= (read_a_signal(RD_TEMP)); // Read LM50
degrees3= (float)((degrees_raw + prev_degrees_raw) / 2);
prev_degrees_raw = degrees_raw;
degrees3 *= .00488; // .00488 = 5 / 1024...convert to voltage
degrees3-= 0.5; //subtract off .5V bias
degrees3/=.01; // 10mV per degree C Floating Point DEGREES
TEMP_HIGH_ERR_ACTIVE = NO;
TEMP_LOW_ERR_ACTIVE = NO;
if(degrees3 > 75)
TEMP_HIGH_ERR_ACTIVE = YES;
if(degrees3 < -40)
TEMP_LOW_ERR_ACTIVE = YES;
restart_wdt();
//==================== Read +24VDC ============================================
//Vf = V(RA2) * 10.3 * 5 / 1024, 1(1 / 10.3 / 5 * 1024) = .0503 volts per step
_24VDC_raw = read_a_signal(RD_24VDC);
_24VDC3 = ((float)_24VDC_raw) * .0503;
_24VDC3 += .7; // reverse polarity diode //floating point 24VDC
_24V_HIGH_ERR_ACTIVE = NO;
_24V_LOW_ERR_ACTIVE = NO;
if(_24VDC3 > 30)
_24V_HIGH_ERR_ACTIVE = YES;
if(_24VDC3 < 18)
_24V_LOW_ERR_ACTIVE = YES;
restart_wdt();
//====================== Read Pump Voltage ======================================
//Vp = V(RA1) * 5 * 5 / 1024, 1(1 / 5 / 5 * 1024) = .0244 volts per step
pump_voltage_raw = read_a_signal(RD_PUMP_VOLTAGE);
pump_voltage3 = (float)pump_voltage_raw * .0244; //floating point PUMP VOLTAGE
_12V_HIGH_ERR_ACTIVE = NO;
_12V_LOW_ERR_ACTIVE = NO;
if(pump_voltage3 > 14)
_12V_HIGH_ERR_ACTIVE = YES;
if(pump_voltage3 < 11)
_12V_LOW_ERR_ACTIVE = YES;
restart_wdt();
//========================= Read Pump Current ======================================
//V(RA5)= 11I I = V(RA5) / 11 * 5 / 1024, 1(11 / 5 * 1024) = .000444 Amps per step
pump_current_raw = read_a_signal(RD_PUMP_CURRENT);
pump_current3 = (float)pump_current_raw * .000444; //floating point PUMP CURRENT
restart_wdt();
//============================= Pump Power ===========================================
pump_voltage3 = pump_voltage3 - (1 * pump_current3); //Subtract off voltage drop across
//current sense resistor (1 Ohm)(Ip)
pump_power3 = pump_current3 * pump_voltage3; //floating point PUMP POWER
temp16 = 0;
while(temp16++ < 0x7A12);
delay_us(1);
} //end of for(;;)
} //End of Main
Posted: Mon Jun 25, 2018 5:32 pm |
Your posted code doesn't compile because of various missing items.
How are we going to solve this if we don't have a compilable test program
to look at ? |
Posted: Mon Jun 25, 2018 6:30 pm |
Along with what PCM P says...
just some observations...
1) why the cryptic 0x7A12 when a simple delay_us(31250); will work and show how long the delay is ?
2) enabling the WDT should only be done in the final version of code
3) since you have ICD=TRUE, that will alter the overall operation of the PIC and the code
4) running the PIC at 4 MHZ seems 'silly' to me, especially with the number of floating point calculations the program has.They along might actually trip the WDT
5) some lines are commented out,well a lot of them,along with a lot of 'includes'. ALL 'commented out' code should be deleted in a posted program. One of those 'less is better' ideas. It helps others concentrate on real code and not get distracted with stuff that isn't happening in the PIC.
6) anytime you have a #use RS232(...options..) you need to add 'ERRORs' to the option list when using the HW UARTs.
7) I don't see where any of the float variables are 'defined ' IE: you have int16 degrees_raw before main() but no float degrees3. I've seen it said here that the compiler requires variables defined( or whatever the term is, I'm NOT a student of C) before main().
8) I don't know(since I seldom use floating points) , but when you do a compare,say if(pump_voltage3 >14), is the '14' converted to the floating point 14.0000 ? To me 14 and 14.0000 can be 2 different numbers within the code and the PIC.
What I do know is that integers, even scaled integers are a LOT faster for the PIC to handle especially using a 'snail slow' 4MHz clock. |
Posted: Tue Jun 26, 2018 12:08 am |
One other comment. All of these:
#include "math.h"
#include "stdlib.h"
Should be _after_ you have setup the delays and RS232.
The standard layout for reliability, is:
Processor include
Fuses
Timing setup
any #pin_select if applicable
#use statements
_then_ the includes.
In this case WDT won't trigger, since with ICD selected this will be turned off. However if it was there could be a problem. The watchdog on this chip (worst case) triggers in just 3.5mSec. Your maths on the reading:
addition
division by 2
multiplication by 0.00488
subtraction
division by 100
at 4Mhz, takes 513uSec+1449uSec+358uSec+523uSec+1449uSec = 4292uSec. Not even allowing any time for actually reading and saving the variables. Result on a real chip the watchdog would trigger.....
Just work in integer. Use signed int16 values. Then:
adc_val=//However you read the adc. You don't actually show the code
adc_val*=49;
adc_val-=5000;
No averaging shown. Honestly better to do this by taking two readings rather than 'carrying forward' the last reading each time.
Now this gives 100 counts per degree. So 125 degrees is 12500 counts. If you think about it the sensor gives 1.75v at 125C. This is 358 counts on the ADC. 358*49 = 17542. Subtract 5000 gives 12542. Nominally 125.42C. One int16 multiplication and one subtraction. Takes 36uSec against the 4.3mSec!... 120* faster (and smaller code as well). Error in the maths only about 0.3%. Given the sensor itself only claims 3% accuracy, far better than is needed. |
Posted: Tue Jun 26, 2018 4:43 am |
Thank Mr T for posting the 'how and why' reply ! Should be a sticky. Anyone wanting to do floating point should read your post !! I knew FP was slow ,but well over 100 TIMES slower !! It should be a real eye opener to every programmer !! |
Zezem
Posted: Tue Jun 26, 2018 8:05 am |
Thanks for the awesome support guys!
To be honest this is my boss's code. He is a smart man but the way he writes code is very old school and can be a pain to follow.
I will talk to him today and make some changes to increase performance. I still don't understand why the compiler would give these floating points weird addresses that are already used by SFRs. I can switch to int16 instead of floats but I'm just curious how this happened?
PORTB location 0xF41
pump_voltage address location = 0xF41
// Filename: GLOBALS.H
// Function Name: na
// Author: PGS
// Description:
// Parameters:
// Input: None.
// Output: None.
int16 current_seconds;
int16 calsw_snapshot;
signed int16 Drift_Array_CH0[16];
signed int16 Drift_Array_CH1[16];
int8 quarter_seconds;
int1 LED_Enable;
int1 comm_ready;
int1 Wait_For_Int;
int8 block0[256];
byte header_byte; // after write to eeprom, holds 0xAA
byte unit_status; // shows current status of unit
byte error_code1; // holds 1st priority err if >0, else none
int8 error_code2;
int8 Device_Code_L,Device_Code_H;
int16 norm_value;
// Global Status Bits
// Permanent Unit Status. Stored to EEPROM. Read from EEPROM at Boot (WR_CALS, RD_CALS)
byte config_byte; // Config Status CH0
// Pat's version has the following statement changed from "UNIT_ZEROED_ONCE".
#bit UNIT_ZEROED_CH0 = config_byte.0 // unit has ONCE been zeroed @ 26C
#bit UNIT_SPANNED_CH0 = config_byte.1 // unit is currently zeroed @ 26C
#bit HOT_ZEROED_CH0 = config_byte.2
#bit COOL_ZEROED_CH0 = config_byte.3
#bit COOL_ZERO_SLOPE_CH0 = config_byte.4
#bit HOT_ZERO_SLOPE_CH0 = config_byte.5
#bit FCR_TABLE_LOADED_CH0 = config_byte.6
//#bit = config_byte.7 // unit has ONCE been spanned
// Pat's version has several bits in config_byte and config2_byte different
// than in Steve's version.
byte config2_byte; // Config Status CH0
#bit UNIT_ZEROED_CH1 = config2_byte.0 // unit has ONCE been zeroed hot
#bit UNIT_SPANNED_CH1 = config2_byte.1
#bit HOT_ZEROED_CH1 = config2_byte.2 // unit is currently zeroed hot
#bit COOL_ZEROED_CH1 = config2_byte.3 // unit currently zeroed cool @ <+3C
#bit COOL_ZERO_SLOPE_CH1 = config2_byte.4
#bit HOT_ZERO_SLOPE_CH1 = config2_byte.5
#bit FCR_TABLE_LOADED_CH1 = config2_byte.6 // COOL bal. factor slope, 1=Pos/0=Neg
// = config2_byte.7 // HOT bal. factor slope, 1=Pos/0=Neg
//Global Temperature Value. This is the DS1775(2's comp) value added to 45. We add 45
//to keep numbers positive over entire operating range(-40 to 85)
//This format is used for all internal calculations.
//Actual temp value (2's comp) is returned as "Unit Temp"
//unsigned int8 degrees; //, last_degrees;
float test;
float degrees;
float pump_voltage;
float _24VDC;
float pump_current;
float pump_power;
float degrees3;
float pump_voltage3;
float _24VDC3;
float pump_current3;
float pump_power3;
//Holds run-time calculated EEPROM checksum
//Compared to EEPROM stored checksum
byte eeprom_checksum;
int8 cmmd_string[4]; // holds RS232 (White Wire) TX & RX bytes
byte _24vdc_rd_value;
//unions used to construct larger variable types from bytes
//Kept gloabal since they are generally read and written over White Wire interface
union word1 // [0] locations for fine adjustment pot (L_byte)
{ // [1] locations for coarse adjustment pot (H_byte)
long word_data; // BAL_value.word_data
char byte_data[2]; // BAL_value.byte_data[0] or [1]
} BAL_value;
union word2
{ // Warm-Up time expressed in seconds (32767 max)
signed long word_data; // Used in "Main"
int8 byte_data[2]; // Configurable over white wire, stored in EEPROM
} WARMUP_value;
union word4
int16 word_data; // CAL_value.word_data
int8 byte_data[2]; // CAL_value.byte_data[0] or [1]
} CAL_value;
union word6
int16 word_data; // RANGE_value.word_data
int8 byte_data[2]; // RANGE_value.byte_data[0] or [1]
} RANGE_value;
union word7
long word_data; // SPAN_value.word_data
char byte_data[2]; // SPAN_value.byte_data[0] or [1]
} SPAN_value;
union word8
long word_data; // SERIAL_num.word_data
char byte_data[2]; // SERIAL_num.byte_data[0] or [1]
} SERIAL_num;
// union word15
// { // used to relay actual pot values in main
// long word_data; // DP_value.word_data
// char byte_data[2]; // DP_value.byte_data[0] or [1]
// } DP_value;
union word16
{ // month and day on which unit was last calibrated
long word_data; // CALIBRATION_DATE.word_data
char byte_data[2]; // CALIBRATION_DATE.byte_data[0] or [1]
} CALIBRATION_DATE;
union word17
{ // used as scratch pad in various functions
long word_data; // scratch_value.word_data
char byte_data[2]; // scratch_value.byte_data[0] or [1]
} SCRATCH_value;
//union word22 Used in "read_ad"
union word64
float word_data; //Used for Ideal Gas Law Calculations (medley.c)
int8 byte_data[4];
} Kelvin_degrees;
//91,92,93,94 used for test parameters
union word95
int16 word_;
int8 byte_[2];
} CH0_Buffer_Size;
union word96
int16 word_;
int8 byte_[2];
} CH1_Buffer_Size;
// GLOBAL FLAG VARIABLES
// Temporary Unit Status bits. Set, cleared, and read during run-time.
// Not stored to EEPROM
// Pat's version has several changes to this section.
byte flag_byte1;
#bit ZERO_SWITCH = flag_byte1.0 // a flag to zero calibrate unit
#bit SPAN_SWITCH = flag_byte1.1 // a flag to span calibrate unit
//#bit HOT_ZERO_SW_CH0 = flag_byte1.2 // a switch to Hot Zero unit
#bit FAULT_ABORT_SWITCH = flag_byte1.3 // a flag to abort fault routine
#bit MAIN_FAULT_SWITCH = flag_byte1.4 // an error occurred in main
#bit CONFIG_BYTE_SWITCH = flag_byte1.5 // a flag to adjust config byte
#bit FOUR_20MA_SWITCH = flag_byte1.6 // a flag to engage in 4-20ma cal
// #bit COOL_ZERO_SW_CH0 = flag_byte1.7 // a switch to Cool Zero unit
byte flag_byte2;
#bit LD_BAL_POT_SWITCH = flag_byte2.0 // a flag to load actual pot value
#bit LD_AGC_POT_SWITCH_0 = flag_byte2.1 // a flag to load actual pot value
#bit LD_SPAN_POT_SWITCH = flag_byte2.2 // a flag to load actual pot value
#bit STORE_SN_SWITCH = flag_byte2.3 // a flag to store SN# in eeprom
#bit STORE_CAL_DATE_SWITCH = flag_byte2.4 // a flag to store cal date info
#bit SOURCE_ENABLED = flag_byte2.5 // a enable's or disable's source
#bit NO_TEMP_ERROR = flag_byte2.6 // a flag to check if temp error
#bit STORE_BITSBYTE_SWITCH = flag_byte2.7 // a flag to store bits byte
byte flag_byte3;
#bit LOAD_TABLE_0_SWITCH = flag_byte3.0 // if set, read in table one
//#bit LOAD_TABLE_1_SWITCH = flag_byte3.1 // if set, read in table two
#bit RD_TABLE_0_CS_SWITCH = flag_byte3.2 // read table one checksum switch
#bit BAL_SLOPE_BIT = flag_byte3.3 // returns slope to calling function
#bit STORE_TARGET_TEMP_SW = flag_byte3.4 // store temp control target temp
#bit ZERO_CH1_SWITCH = flag_byte3.5 // a flag to...
#bit SPAN_CH1_SWITCH = flag_byte3.6 // a flag to...
//#bit CH_SELECT = flag_byte3.7 // 0=CH0, 1=CH1
byte flag_byte4;
//#bit = flag_byte4.0
//#bit = flag_byte4.1
//#bit = flag_byte4.2
//#bit = flag_byte4.3
//#bit = flag_byte4.4
//#bit = flag_byte4.5
#bit HOT_ZERO_SW_CH0 = flag_byte4.6 //
#bit COOL_ZERO_SW_CH0 = flag_byte4.7 //
byte flag_byte5;
//#bit RD_TABLE_1_CS_SWITCH = flag_byte5.0
#bit HOT_ZERO_SW_CH1 = flag_byte5.1
#bit COOL_ZERO_SW_CH1 = flag_byte5.2
#bit OK_TO_HZ = flag_byte5.3 //Temp OK, Unit Status OK for Hot Zero
#bit OK_TO_CZ = flag_byte5.4
#bit SELF_TEST_SW = flag_byte5.5
#bit ABORT_TEST_SW = flag_byte5.6
#bit Abort_Warm_Up = flag_byte5.7
byte flag_byte6;
#bit Reset_CH0_Buf_Zero = flag_byte6.0
#bit Reset_CH0_Buf_Span = flag_byte6.1
#bit Reset_CH1_Buf_Zero = flag_byte6.2
#bit Reset_CH1_Buf_Span = flag_byte6.3
#bit Reset_CH0_Drift_Array = flag_byte6.4
#bit Reset_CH1_Drift_Array = flag_byte6.5
#bit Err_CH0 = flag_byte6.6
#bit Err_CH1 = flag_byte6.7
byte flag_byte7;
#bit Pres_Table_Loaded_CH0 = flag_byte7.0 //Run time flag, updated
// #bit Pres_Table_Loaded_CH1 = flag_byte7.1 //during "load_cal_factors"
#bit Valid_Pres_Input = flag_byte7.2
#bit Pres_En_Global_CH0 = flag_byte7.3
// #bit WR_COMP_SWITCH = flag_byte7.4
// #bit WR_SPAN_CH0_SW = flag_byte7.5
// #bit WR_SPAN_CH1_SW = flag_byte7.6
// #bit WR_COMP_STATUS = flag_byte7.7
byte flag_byte8;
#bit RANGE_SWITCH = flag_byte8.0 // 1=Write new Range(EEPROM)
#bit CAL_VALUE_SWITCH = flag_byte8.1 // 1=Write new Cal Value
#bit load_cal_fact = flag_byte8.2 //
//#bit = flag_byte8.3
//#bit = flag_byte8.4
#bit Store_Fact_Param = flag_byte8.5 //Copies Data E2 to Prog Mem
#bit Restore_Fact_Param = flag_byte8.6 //Copies Prog Mem to Data E2
//#bit = flag_byte8.3 //
byte flag_byte9;
#bit checksum_ready = flag_byte9.0 //Used in read table checksum
#bit ZERO_CH0_FLAG = flag_byte9.1 //Zero Command zeros both channels
//This flag set after CH1 Zero...signals CH0 Zero
#bit COOL_ZERO_CH0_FLAG = flag_byte9.2
//This flag set after CH1 Cool Zero...signals CH1 Cool Zero
#bit HOT_ZERO_CH0_FLAG = flag_byte9.3
//This flag set after CH1 Hot Zero...signals CH0 Hot Zero
//#bit WR_Drift_Tables_CH0_0 = flag_byte9.4 //Drift Table write done in 4 sections
//#bit WR_Drift_Tables_CH0_1 = flag_byte9.5 //
//#bit WR_Drift_Tables_CH1_0 = flag_byte9.6 //
//#bit WR_Drift_Tables_CH1_1 = flag_byte9.7 //
// Steve added. This was missing from Pat's file.
unsigned int8 flags_read; // General purpose flags set by slave and read
// by master.
#bit ee_written = flags_read.0 // Flag to tell master that slave had to
// write defaults to its EEPROM because
// of bad checksum.
// Everything from here on, Pat added.
byte flag_byte10; //Critical Faults
#bit _12V_HIGH_ERR_ACTIVE = flag_byte10.0
#bit _12V_LOW_ERR_ACTIVE = flag_byte10.1
#bit No_Pressure_Signal = flag_byte10.2
#bit TEMP_HIGH_ERR_ACTIVE = flag_byte10.3
#bit TEMP_LOW_ERR_ACTIVE = flag_byte10.4
#bit _24V_HIGH_ERR_ACTIVE = flag_byte10.5
#bit _24V_LOW_ERR_ACTIVE = flag_byte10.6
#bit MPL115A2_RD_ERR_ACTIVE = flag_byte10.7
byte flag_byte11; //Recoverable Faults
//#bit zero_drift = flag_byte11.0 //Zero drift
#bit AGC_POT_MIN = flag_byte11.1
#bit AGC_POT_MAX = flag_byte11.2
#bit delayed_zero_drift_0 = flag_byte11.3
#bit delayed_zero_drift_1 = flag_byte11.4
//#bit = flag_byte11.5
//#bit = flag_byte11.6
//#bit = flag_byte11.7
byte flag_byte12;
#bit Optical_Problem = flag_byte12.0
#bit CRITICAL_FAULT_SW = flag_byte12.1
//#bit Comp_out_of_range = flag_byte12.2
byte flag_byte13;
#bit Wr_Zero_Param = flag_byte13.0 //Flags for EEProm Writes
#bit Wr_Span_Param = flag_byte13.1
#bit Wr_Hot_Zero_Param_CH0 = flag_byte13.2
#bit Wr_Cool_Zero_Param_CH0 = flag_byte13.3
#bit Wr_Zero_Param_CH1 = flag_byte13.4
#bit Wr_Span_Param_CH1 = flag_byte13.5
#bit Wr_Hot_Zero_Param_CH1 = flag_byte13.6
#bit Wr_Cool_Zero_Param_CH1 = flag_byte13.7
byte flag_byte14;
#bit WR_Four_Ma_Value = flag_byte14.0
#bit WR_Span_Ma_Value = flag_byte14.1
#bit WR_COMP_SWITCH = flag_byte14.2
#bit WR_SPAN_CH0_SW = flag_byte14.3
#bit WR_SPAN_CH1_SW = flag_byte14.4
#bit WR_COMP_STATUS = flag_byte14.5
#bit WR_Drift_Tables_CH0_0 = flag_byte14.6 //Drift Table write done in 4 sections
#bit WR_Drift_Tables_CH0_1 = flag_byte14.7 //
byte flag_byte15;
#bit WR_Drift_Tables_CH1_0 = flag_byte15.0 //
#bit WR_Drift_Tables_CH1_1 = flag_byte15.1 //
byte warning_flags;
#bit interfering_gas = warning_flags.0
#bit Calibration_Needed = warning_flags.1
//Analyt-0: Primary Analytical optical channel...always present
//Analyt-1: 2nd Analytical channel...used to comp Analyt-1 or Independant 2nd gas measurement
byte comp_status; //Optical Compensation
#bit COMP_SWITCH = comp_status.2 //Analyt-1 used to Comp Analyt-0, 1=ON, 0=OFF
byte unit_settings;
#bit IGL_SWITCH = unit_settings.0 // 1=Ideal Gas Law Comp Enabled
// #bit = unit_settings.1
#bit CHl_Active = unit_settings.2 // 1= CH1 Analyt is Active
#bit single_channel = unit_settings.3 // 1= Single Gas Output
#bit Drift_Tracking = unit_settings.4 // 1=On, 0=Off
#bit Suppress = unit_settings.5 //Suppress low output levels...1=On, 0=Off
#bit Comp_Warn_or_Err = unit_settings.6 //Large Comp Value Result...Warning = 1, Err = 0
#bit Cal_Warning_Mode = unit_settings.7 // 1 = ON, 0 = Off
byte I2C_STATUS;
#bit MPL115A2_err = I2C_STATUS.0 //I2C Com Error Pres/Temp Sensor
//int16 pv_out; // Gas concentration.
//int8 twos_comp_degrees_out;
unsigned int8 st_talk_attempts, st_talk;
byte i2c_error;
enum
ST_STARTUP, /* In this state the Master attempts
to send startup information to the
Slave. */
ST_NORMAL = 2, /* Normal state. The Master has sent
the startup information earlier and
now is sending and receiving Slave
updates. */
ST_MALFUNCTION /* Malfunction state. Number of
attempts to write to Slave has
expired. Master will continue
trying but will set an error code
of ERR_NO_SLAVE */
int8 master_ww_state; // Master's HART/white-wire state machine.
// 0 = idle.
// 1 = got command.
// 2 = wrote response.
//unsigned int8 ww_cmmd_string[4]; // Stores command string used
// when HART is used to
// communicate the white wire
// command.
//unsigned int8 loop_current_mode = 0;
// Determines whether output current
// is active (value = 0) or parked
// (value = 1).
// HART units code definitions.
#define TEMPERATURE_CODE 32 // Degree C.
#define PRESSURE_CODE 6 // psi.
#define PPM_CODE 139 // parts per million.
#define PLEL_CODE 161 // percent of least explosive level.
#define PPB_CODE 169 // parts per billion.
#define VOLUME_PERCENT_CODE 149 // percent volume.
#define MILLIGRAM_PER_LITER_CODE 170
// Pressure temperature sensor:
#define PT_I2C_ADDR 0x60 // I2C address.
#define TEMPERATURE_ADDER 5 // amount to add to temp sensor readings.
#define FCOEFF 0.98 // Filter coefficient to filter pressure readings.
//unsigned int8 ptcomp[12];
//float a0_float, b1_float, b2_float, c12_float, c11_float, c22_float;
Man I have a dream to one day be half as smart as some of you guys
I didn't include all the files because they are quiet large. [/quote] |
Posted: Tue Jun 26, 2018 9:19 am |
We still don't have the code to compile it. There could easily be something in one of your unpublished files causing the problem. Any #locate statements?. Any #byte or #word statements?.
You need ideally to generate a smaller version of the code that you can distribute, which shows the problem, so we can test and see if the problem is the same on a different compiler.
Do a search yourself in the files. Any statement lines involving 'pump_voltage'?. |
Zezem
Posted: Tue Jun 26, 2018 9:36 am |
Quote: | Any #locate statements?. Any #byte or #word statements?. |
Ok so there is a header file with #bit declarations that might be the problem:
// Registers.
// Created for 18f26k22 on 12-16-2011 --- Steve A.
#byte ANSELA = 0xF38
#byte ANSELB = 0xF39
#byte ANSELC = 0xF3A
#byte ANSELD = 0xF3B
#byte ANSELE = 0xF3C
#byte PMD2 = 0xF3D
#byte PMD1 = 0xF3E
#byte PMD0 = 0xF3F
#byte VREFCON2 = 0xF40
#byte VREFCON1 = 0xF41
#byte VREFCON0 = 0xF42
#byte CTMUICON = 0xF43
#byte CTMUCONL = 0xF44
#byte CTMUCONH = 0xF45
#byte SRCON1 = 0xF46
#byte SRCON2 = 0xF47
#byte CCPTMRS1 = 0xF48
#byte CCPTMRS0 = 0xF49
#byte T6CON = 0xF4A
#byte PR6 = 0xF4B
#byte TMR6 = 0xF4C
#byte T5GCON = 0xF4D
#byte T5CON = 0xF4E
#byte TMR5L = 0xF4F
#byte TMR5H = 0xF50
#byte T4CON = 0xF51
#byte PR4 = 0xF52
#byte TMR4 = 0xF53
#byte CCP5CON = 0xF54
#byte CCPR5L = 0xF55
#byte CCPR5H = 0xF56
#byte CCP4CON = 0xF57
#byte CCPR4L = 0xF58
#byte CCPR4H = 0xF59
#byte PSTR3CON = 0xF5A
#byte ECCP3AS = 0xF5B
#byte PWM3CON = 0xF5C
#byte CCP3CON = 0xF5D
#byte CCPR3L = 0xF5E
#byte CCPR3H = 0xF5F
#byte SLRCON = 0xF60
#byte WPUB = 0xF61
#byte IOCB = 0xF62
#byte PSTR2CON = 0xF63
#byte ECCP2AS = 0xF64
#byte PWM2CON = 0xF65
#byte CCP2CON = 0xF66
#byte CCPR2L = 0xF67
#byte CCPR2H = 0xF68
#byte SSP2CON3 = 0xF69
#byte SSP2MSK = 0xF6A
#byte SSP2CON2 = 0xF6B
#byte SSP2CON1 = 0xF6C
#byte SSP2STAT = 0xF6D
#byte SSP2ADD = 0xF6E
#byte SSP2BUF = 0xF6F
#byte BAUDCON2 = 0xF70
#byte RCSTA2 = 0xF71
#byte TXSTA2 = 0xF72
#byte TXREG2 = 0xF73
#byte RCREG2 = 0xF74
#byte SPBRG2 = 0xF75
#byte SPBRGH2 = 0xF76
#byte CM2CON1 = 0xF77
#byte CM2CON0 = 0xF78
#byte CM1CON0 = 0xF79
#byte PIE4 = 0xF7A
#byte PIR4 = 0xF7B
#byte IPR4 = 0xF7C
#byte PIE5 = 0xF7D
#byte PIR5 = 0xF7E
#byte IPR5 = 0xF7F
#byte PORTA = 0xF80
#byte PORTB = 0xF81
#byte PORTC = 0xF82
#byte PORTD = 0xF83
#byte PORTE = 0xF84
#byte LATA = 0xF89
#byte LATB = 0xF8A
#byte LATC = 0xF8B
#byte LATD = 0xF8C
#byte LATE = 0xF8D
#byte TRISA = 0xF92
#byte TRISB = 0xF93
#byte TRISC = 0xF94
#byte TRISD = 0xF95
#byte TRISE = 0xF96
#byte OSCTUNE = 0xF9B
#byte HLVDCON = 0xF9C
#byte PIE1 = 0xF9D
#byte PIR1 = 0xF9E
#byte IPR1 = 0xF9F
#byte PIE2 = 0xFA0
#byte PIR2 = 0xFA1
#byte IPR2 = 0xFA2
#byte PIE3 = 0xFA3
#byte PIR3 = 0xFA4
#byte IPR3 = 0xFA5
#byte EECON1 = 0xFA6
#byte EECON2 = 0xFA7
#byte EEDATA = 0xFA8
#byte EEADR = 0xFA9
#byte EEADRH = 0xFAA
#byte RCSTA1 = 0xFAB
#byte TXSTA1 = 0xFAC
#byte TXREG1 = 0xFAD
#byte RCREG1 = 0xFAE
#byte SPBRG1 = 0xFAF
#byte SPBRGH1 = 0xFB0
#byte T3CON = 0xFB1
#byte TMR3L = 0xFB2
#byte TMR3H = 0xFB3
#byte T3GCON = 0xFB4
#byte ECCP1AS = 0xFB6
#byte PWM1CON = 0xFB7
#byte BAUDCON1 = 0xFB8
#byte PSTR1CON = 0xFB9
#byte T2CON = 0xFBA
#byte PR2 = 0xFBB
#byte TMR2 = 0xFBC
#byte CCP1CON = 0xFBD
#byte CCPR1L = 0xFBE
#byte CCPR1H = 0xFBF
#byte ADCON2 = 0xFC0
#byte ADCON1 = 0xFC1
#byte ADCON0 = 0xFC2
#byte ADRESL = 0xFC3
#byte ADRESH = 0xFC4
#byte SSP1CON2 = 0xFC5
#byte SSP1CON1 = 0xFC6
#byte SSP1STAT = 0xFC7
#byte SSP1ADD = 0xFC8
#byte SSP1BUF = 0xFC9
#byte SSP1MSK = 0xFCA
#byte SSP1CON3 = 0xFCB
#byte T1GCON = 0xFCC
#byte T1CON = 0xFCD
#byte TMR1L = 0xFCE
#byte TMR1H = 0xFCF
#byte RCON = 0xFD0
#byte WDTCON = 0xFD1
#byte OSCCON2 = 0xFD2
#byte OSCCON = 0xFD3
#byte T0CON = 0xFD5
#byte TMR0L = 0xFD6
#byte TMR0H = 0xFD7
#byte STATUS = 0xFD8
#byte FSR2L = 0xFD9
#byte FSR2H = 0xFDA
#byte PLUSW2 = 0xFDB
#byte PREINC2 = 0xFDC
#byte POSTDEC2 = 0xFDD
#byte POSTINC2 = 0xFDE
#byte INDF2 = 0xFDF
#byte BSR = 0xFE0
#byte FSR1L = 0xFE1
#byte FSR1H = 0xFE2
#byte PLUSW1 = 0xFE3
#byte PREINC1 = 0xFE4
#byte POSTDEC1 = 0xFE5
#byte POSTINC1 = 0xFE6
#byte INDF1 = 0xFE7
#byte WREG = 0xFE8
#byte FSR0L = 0xFE9
#byte FSR0H = 0xFEA
#byte PLUSW0 = 0xFEB
#byte PREINC0 = 0xFEC
#byte POSTDEC0 = 0xFED
#byte POSTINC0 = 0xFEE
#byte INDF0 = 0xFEF
#byte INTCON3 = 0xFF0
#byte INTCON2 = 0xFF1
#byte INTCON = 0xFF2
#byte PRODL = 0xFF3
#byte PRODH = 0xFF4
#byte TABLAT = 0xFF5
#byte TBLPTRL = 0xFF6
#byte TBLPTRH = 0xFF7
#byte TBLPTRU = 0xFF8
#byte PCL = 0xFF9
#byte PCLATH = 0xFFA
#byte PCLATU = 0xFFB
#byte STKPTR = 0xFFC
#byte TOSL = 0xFFD
#byte TOSH = 0xFFE
#byte TOSU = 0xFFF
// PORT BIT DEFINITIONS
//**** Port A
//#bit = PORTA.0 //Pin 2 AN0
#bit Pump_Voltage = PORTA.1 //Pin 3 AN1
#bit _24VDC = PORTA.2 //Pin 4 AN2
#bit Temperature_LM50 = PORTA.3 //Pin 5 AN3
//#bit = PORTA.4 //Pin 6
#bit Pump_Current = PORTA.5 //Pin 7 AN4
//#bit = PORTA.6 //Pin 10
//#bit = PORTA.7 //Pin 9
//**** Port B
//#bit = PORTB.0 //Pin 21
#bit WRITE = PORTB.1 //Pin 22
//#bit = PORTB.2 //Pin 23
//#bit = PORTB.3 //Pin 24
//#bit = PORTB.4 //Pin 25
//#bit = PORTB.5 //Pin 26
//#bit = PORTB.6 //Pin 27
//#bit = PORTB.7 //Pin 28
//**** Port C
#bit READ = PORTC.0 //Pin 11
//#bit Fan_Tach = PORTC.1
//#bit = PORTC.2
#define _SCL PIN_C3
#define _SDA PIN_C4
//#bit = PORTC.5
//#bit = PORTC.6
#bit Test_Pin = PORTC.7 //Pin 18
//STATUS register bits
#BIT CARRY = STATUS.0
#BIT DC = STATUS.1
#BIT ZERO = STATUS.2
#BIT PWR_DOWN = STATUS.3
#BIT TIME_OUT = STATUS.4
#BIT RP0 = STATUS.5
#BIT RP1 = STATUS.6
#BIT IRP = STATUS.7
//INTCON register bits
#BIT RBIF = INTCON.0
#BIT INTF = INTCON.1
#BIT T0IF = INTCON.2
#BIT RBIE = INTCON.3
#BIT INTE = INTCON.4
#BIT T0IE = INTCON.5
#BIT PEIE = INTCON.6
#BIT GIE = INTCON.7
// PIR1 register bits
#BIT TMR1IF = PIR1.0
#BIT TMR2IF = PIR1.1
#BIT CCP1IF = PIR1.2
#BIT SSPIF = PIR1.3
#BIT TXIF = PIR1.4
#BIT RCIF = PIR1.5
#BIT ADIF = PIR1.6
#BIT PSPIF = PIR1.7
// PIR2 register bits
#BIT CCP2IF = PIR2.0
/* T1CON register bits
#BIT TMR1ON = T1CON.0
#BIT TMR1CS = T1CON.1
#BIT T1SYNC_ = T1CON.2
#BIT T1OSCEN = T1CON.3
#BIT T1CKPS0 = T1CON.4
#BIT T1CKPS1 = T1CON.5
// T1CON register bits
#BIT T1RD16 = T1CON.1
#BIT T1SOSCEN = T1CON.3
#BIT TMR1CS0 = T1CON.6
#BIT TMR1CS1 = T1CON.7
// T3CON register bits
#BIT TMR3ON = T3CON.0
#BIT T3RD16 = T3CON.1
#BIT T3SYNC_ = T3CON.2
#BIT T3SOSCEN = T3CON.3
#BIT T3CKPS0 = T3CON.4
#BIT T3CKPS1 = T3CON.5
#BIT TMR3CS0 = T3CON.6
#BIT TMR3CS1 = T3CON.7
// T2CON register bits
#BIT T2CKPS0 = T2CON.0
#BIT T2CKPS1 = T2CON.1
#BIT TMR2ON = T2CON.2
#BIT TOUTPS0 = T2CON.3
#BIT TOUTPS1 = T2CON.4
#BIT TOUTPS2 = T2CON.5
#BIT TOUTPS3 = T2CON.6
// SSPCON register bits
// #BIT SSPM0 = SSPCON1.0
// #BIT SSPM1 = SSPCON1.1
// #BIT SSPM2 = SSPCON1.2
// #BIT SSPM3 = SSPCON1.3
// #BIT CKP = SSPCON1.4
// #BIT SSPEN = SSPCON1.5
// #BIT SSPOV = SSPCON1.6
// #BIT WCOL = SSPCON1.7
// RCSTA register bits
#BIT RX9D = RCSTA1.0
#BIT OERR = RCSTA1.1
#BIT FERR = RCSTA1.2
#BIT ADDEN = RCSTA1.3
#BIT CREN = RCSTA1.4
#BIT SREN = RCSTA1.5
#BIT RX9 = RCSTA1.6
#BIT SPEN = RCSTA1.7
// CCP1CON register bits
#BIT CCP1M0 = CCP1CON.0
#BIT CCP1M1 = CCP1CON.1
#BIT CCP1M2 = CCP1CON.2
#BIT CCP1M3 = CCP1CON.3
#BIT CCP1Y = CCP1CON.4
#BIT CCP1X = CCP1CON.5
// CCP2CON register bits
#BIT CCP2M0 = CCP2CON.0
#BIT CCP2M1 = CCP2CON.1
#BIT CCP2M2 = CCP2CON.2
#BIT CCP2M3 = CCP2CON.3
#BIT CCP2Y = CCP2CON.4
#BIT CCP2X = CCP2CON.5
// ADCON0 register bits
#BIT ADON = ADCON0.0
#BIT GO = ADCON0.1
#BIT DONE_ = ADCON0.1
#BIT CHS0 = ADCON0.2
#BIT CHS1 = ADCON0.3
#BIT CHS2 = ADCON0.4
#BIT CHS3 = ADCON0.5
//#BIT = ADCON0.6
//#BIT = ADCON0.7
// ADCON2 register bits
#BIT ADCS0 = ADCON2.0
#BIT ADCS1 = ADCON2.1
#BIT ADCS2 = ADCON2.2
#BIT ACQT0 = ADCON2.3
#BIT ACQT1 = ADCON2.4
#BIT ACQT2 = ADCON2.5
//#BIT = ADCON2.6
#BIT ADFM = ADCON2.7
// T0CON register bits
#BIT T0PS0 = T0CON.0
#BIT T0PS1 = T0CON.1
#BIT T0PS2 = T0CON.2
#BIT PSA = T0CON.3
#BIT T0SE = T0CON.4
//#BIT RTE = T0CON.4
#BIT T0CS = T0CON.5
//#BIT RTS = T0CON.5
#BIT T08BIT = T0CON.6
//#BIT INTEDG = T0CON.6
#BIT TMR0ON = T0CON.7
//#BIT RBPU_ = T0CON.7
// TRISA register bits
#BIT TRIS_A0 = TRISA.0
#BIT TRIS_A1 = TRISA.1
#BIT TRIS_A2 = TRISA.2
#BIT TRIS_A3 = TRISA.3
#BIT TRIS_A4 = TRISA.4
#BIT TRIS_A5 = TRISA.5
#BIT TRIS_A6 = TRISA.6
#BIT TRIS_A7 = TRISA.7
// TRISB register bits
#BIT TRIS_B0 = TRISB.0
#BIT TRIS_B1 = TRISB.1
#BIT TRIS_B2 = TRISB.2
#BIT TRIS_B3 = TRISB.3
#BIT TRIS_B4 = TRISB.4
#BIT TRIS_B5 = TRISB.5
#BIT TRIS_B6 = TRISB.6
#BIT TRIS_B7 = TRISB.7
// TRISC register bits
#BIT TRIS_C0 = TRISC.0
#BIT TRIS_C1 = TRISC.1
#BIT TRIS_C2 = TRISC.2
#BIT TRIS_C3 = TRISC.3
#BIT TRIS_C4 = TRISC.4
#BIT TRIS_C5 = TRISC.5
#BIT TRIS_C6 = TRISC.6
#BIT TRIS_C7 = TRISC.7
// PIE1 register bits
#BIT TMR1IE = PIE1.0
#BIT TMR2IE = PIE1.1
#BIT CCP1IE = PIE1.2
#BIT SSPIE = PIE1.3
#BIT TXIE = PIE1.4
#BIT RCIE = PIE1.5
#BIT ADIE = PIE1.6
#BIT PSPIE = PIE1.7
// TXSTA register bits
#BIT TXD8 = TXSTA1.0
#BIT TRMT = TXSTA1.1
#BIT BRGH = TXSTA1.2
#BIT SYNC = TXSTA1.4
#BIT TXEN = TXSTA1.5
#BIT TX89 = TXSTA1.6
#BIT CSRC = TXSTA1.7
// ADCON1 register bits
#BIT PCFG0 = ADCON1.0
#BIT PCFG1 = ADCON1.1
#BIT PCFG2 = ADCON1.2
Zezem
Posted: Tue Jun 26, 2018 9:48 am |
Figured out the problem after posting the last reply.
Someone thought it was a good idea to use the same variable names
float pump_voltage, _24VDC, pump_current;
Thanks for all your help!! I got educated on floating points that i will use for all future projects!! |
Posted: Tue Jun 26, 2018 11:24 am |
As I said:
Hopefully that search was what led to finding it....
Aargh.
That is one reason why when working on reasonably serious code, I like to have the names 'self indicate'. So a 'bit' would normally always be xxx_b. A type would be xxx_t. etc.. It helps to avoid that sort of problem. |
Posted: Tue Jun 26, 2018 1:12 pm |
Gee when I started this 'microcomputer' gig, variables were limited to TWO characters when using the 'high level' language of Microsoft BASIC ! When I used COBOL every variable was coded as xxx_yyy_zzz.
Nowadays you can probably use 254 characters to name a variable so it is sad (and frustrating) to see the 'fun' the OP has had with this code.
Posted: Thu Jun 28, 2018 6:11 pm |
Zezem wrote: | Figured out the problem after posting the last reply.
Also keep in mind there is a #case directive you can use to enforce casing. It would have saved you on 2 of those (they would have been separate variables), but the _24VDC would have still been a problem. |
